My system is suffering a sort of mismatching.
I have a Watchmon Core, connected to a Victron Cerbo GX.
As a result of upgrading firmware (new is 14.3.67) and toolkit (2.17.54), the target values transmitted to the cerbo are the ones I put, but divided per ten.
Then, cerbo values CVL, CCL and DCL are so low, that the system does not charge the battery.
I can only upload one photo.

Hi JJLozano,

Sounds like you set your scaling values wrong. Some inverters want 200 to represent 20.0V others want it to represent 200V.

First things first, upgrade to our latest build 55, it is a lot more stable than 54.

After that, run the setup wizard again. I can see you have quite a few things misconfigured, like bypass threshold all the way up at 3.65V. Your cells will never balance. Here’s a video that goes over our balancing algorithms and how you should set everything up:

I’m confident you will be much happier after the above steps :slight_smile:

Let me know if you have any troubles!