WM5. FW 5.10.104
Toolkit 2.17.57
CCGX FW 3.55 (highest allowed on CCGX)
DVCC on
Deployed 7/2022, 23.3kWh 14S NMC battery.
Off grid, so ESS is pure insanity for me. The Victron instructions on your site are just plain wrong. This was well before DVCC was auto-enabled when it sensed an attached Batrium.
No grid interaction, so that’s why I confessed to potentially missing something in this context. I can only recognize ESS when it’s spoken. I can’t speak it.
MPPT is hooked to GX. CHARGE control limit (CCL) 0A = the GX does not alloy CHARGING. It’s not perfect, but they seem to favor a very slight draw (<1A draw from the battery), but rapid load changes can cause very brief charging.
The only thing that shuts down the MPPT completely is critical temp and voltage. Expansion board opens the circuit to the MPPT control relay.
It is my understanding that this is the expected behavior. It’s limiting CHARGE current, not MPPT output. Even on a lead acid battery, you can set a CCL in DVCC, and it will prevent all GX connected chargers from exceeding the CCL current. So you can limit your puny FLA battery to 30A charge, but still get the max 100A out of your MPPT.
On another matter… I have found what I suspect is a bug, but it offers the functionality I want. I would like to tell you about it, but I don’t want it taken away… 
Unrelated to the bug, but kinda… The Batrium system is complex, so I don’t grasp a lot of it, mostly because I don’t need it, and because I’m old and lazy, and I can’t figure things out like I used to.
It’s my understanding that Batrium was developed primarily around 3.7V chemistry and has needed adaptations to make it more suitable for LFP as you don’t want low current overcharge holding LFP at peak voltage.
Given that there is substantial cycle life improvement by reducing depth of the charge/discharge of NCA/LMO/NMC chemistries (20%-75%), there HAS to be a way to manage the battery thusly and do so automatically. I mean surely someone has asked for this in the past?
For my particular variation of NMC chemistry (NMC-LMO blend), 3.92V is 75% SoC. I never want to go above this unless I know I need the extra capacity, and I rarely do. The site rarely uses more than 10kWh/day and with 6kW PV available in sunny AZ, I don’t use up a lot of battery capacity. Since I can’t figure out how to sync to a value at a given target (only 100%), I’m continuously resetting my SoC back down to 75% every week or so as it creeps up even without balancing.
Thoughts?